connecting Mitsubishi via RS485
#9
Hello Carsten,

if you want to use RS485 for communication then you need to know which device is the master and which the slave. This is how Modbus RTU works.

I suppose your PLC is the modbus slave , or isn't it? I don't know. You need to get this information from the PLC. Here I can't help.

netPI - depending on the Node-RED node you use - can be either master or slave on RS-485 NPIX.

A statement to the RS485 LEDs: Since this interface is just solving the physics there is in no way a definition whether the protocol Modbus goes across it, nor the protocol M-Bus, Bacnet or any other serial protocol. This is all decided by the application side that is using the NPIX module during runtime ... so then a question back: how shall then the LED automatically know how to behave on the different type of protocols in use and when to be red or green or on and off. This can only be the responsibility as well of the application that uses the interface. This is why the LED of the NPIX Modules are free programmable.

I have no working example of Modbus RTU communication - respectively a Node-RED example. In best case it is just using the preinstalled Modbus client/master node within the Node-RED node catalogue. Client/Master if your Mitsubishi PLC is slave/server ... which you need to get out from somewhere as information

Thx
Armin
You never fail until you stop trying.“, Albert Einstein (1879 - 1955)

  Reply


Messages In This Thread
connecting Mitsubishi via RS485 - by COswald - January-2nd-2020, 02:40 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-2nd-2020, 03:20 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-2nd-2020, 08:25 PM
RE: connecting Mitsubishi via RS485 - by COswald - January-3rd-2020, 12:50 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-3rd-2020, 01:09 PM
RE: connecting Mitsubishi via RS485 - by COswald - January-6th-2020, 02:00 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-6th-2020, 02:07 PM
RE: connecting Mitsubishi via RS485 - by COswald - January-13th-2020, 03:36 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-13th-2020, 03:50 PM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-13th-2020, 03:53 PM
RE: connecting Mitsubishi via RS485 - by COswald - January-14th-2020, 10:06 AM
RE: connecting Mitsubishi via RS485 - by Armin@netPI - January-14th-2020, 10:58 AM

Possibly Related Threads…
Thread Author Replies Views Last Post
  NPIX-RS485 with auto direction control now available Armin@netPI 11 8,609 May-15th-2020, 10:46 PM
Last Post: EnergyKonnex
  Problems with the communication of the RS485 interface PeterL. 9 6,768 April-28th-2020, 02:53 PM
Last Post: Armin@netPI
  connec Mitsubishi using Modbus/TCP or SLMP COswald 1 2,770 January-8th-2020, 03:24 PM
Last Post: Armin@netPI
  Dual RS485 Ports primmer 2 3,116 September-25th-2019, 09:43 AM
Last Post: primmer
  Connecting two LAN network segments Lingyue 2 7,177 September-9th-2019, 07:45 AM
Last Post: Armin@netPI

Forum Jump:


Users browsing this thread: 1 Guest(s)