Hello I am currently using the netHAT product as an EtherNet/IP adapter where I am also running the example application that increments the 32 bytes of T2O data by 1 every second. I have it connected to a scanner and can see the T2O data increasing each second. However, the first four bytes seem to never change, always stuck on 1, 0, 0, 0 as shown in the screen shot provided. The T2O data thats printed to the terminal on the PI looks fine, its just when the data is sent over to the scanner. I was just wondering anyone knows if there is a fix for this?
Well I am not an Ethernet/IP expert but I found the following remark in one of our documentations
Run/Idle Mode for Realtime Transfer
The Run/Idle header is a 32-bit field added to packets flowing in the O2T or T2O direction. In O2T direction it contains several bits of status info. Of primary interest is the least significant bit, which reflects the mode of the connection originator. When this bit is set it means the originator is in Run mode, actively controlling I/O. When cleared this indicates that the originator is in Idle mode, not actively controlling the I/O. Run/Idle is not counted as part of the configured data size in the EDS Connection Manager section. It is counted in the FwdOpen Message O2T and T2O sizes however.
It seems to me that these 4 bytes are quite normal for an Ethernet/IP based communcation.